Quote from Guest on 3 July 2026, 10:00 amI need to set up high and low alarms on several of our temperature sensors. How does alarm configuration work in Accord Designer?
I need to set up high and low alarms on several of our temperature sensors. How does alarm configuration work in Accord Designer?
Quote from Tim S on 3 July 2026, 10:00 amAlarms are configured at the program level in Accord Designer. Each alarm has an Enabler Type and Enabler Reference (the condition that triggers the alarm) and an Alarm Type. Alarms can be enabled within specific steps and will place the associated Unit or Program into an alarm state when triggered. All alarms are automatically logged by Accord Server. Analog Input alarm levels include High High, High, Low, and Low Low setpoints.
Alarms are configured at the program level in Accord Designer. Each alarm has an Enabler Type and Enabler Reference (the condition that triggers the alarm) and an Alarm Type. Alarms can be enabled within specific steps and will place the associated Unit or Program into an alarm state when triggered. All alarms are automatically logged by Accord Server. Analog Input alarm levels include High High, High, Low, and Low Low setpoints.